l know we have some experts here. The situation is, my place in the Bahamas is without grid power now and will likely be that way for some time. I’m back feeding with a small generator through 2 outlets such that I’m energizing both legs in the panel. The question is regarding phasing. I have 3 mini splits wired for 220. Both legs will be hot, but in the same phase I assume, so how will that affect them. Will they essentially get no power, or will they only feel 110, or will they burn up? I can do without the AC, but the question is what happens if I try them?
Your generator will need to output in 240v 2-pole single phase in order to get the splits to work Look for an L14-20 or L14-30 twist lock receptacle on the gennie.
Honda 2000 gen. No 240. Easy enough to power both sides of the panel, but I assume having both legs “in phase” or “out of phase”, which ever term is correct, means I won’t have 240. Will the AC’s just not work, or will they pop? Nothing else in the house needs 240.
Yep not going to work. The 120Vs will be in phase. Turn off all 240V breakers while doing this as well as the main feed Also, be careful of current draw. The wires from the genny to the panel will see all current pulled by all other circuits. Most breakers are bi-directional but check. If you can try to plug into a 20a circuit instead of the normal 15a
Turn all the 240vac breakers off to isolate each side of the panel, your 2 generators aren't phased together so your voltage being supplied is unknown and may vary
I’m only reading one gennie backfeeding through two out-of-phase circuits to energize both phases of the panel, but yes, you will not have more than 120v. Overcurrent protection on the gennie will pop if the draw gets too high, but don’t cheap out on the cords you use, and make them as short as possible. And consider putting a bypass switch and flanged inlet in to keep linemen from getting killed if you whoops and forget to turn the main breaker off.
Do a basic diagram for us so we can completely understand what's going on here. Don't care if you sketch it on a napkin. Give us something
You're right, for some reason I was thinking he had (2) 120vac generators trying to feed a 240vac panel. Not sure why I got that in my head since it was clearly stated.
Sounds like one generator to me too. Not gonna power much simultaneously. The 2000 provides 1600 watts at 120v while running so your combined draw in the house has to be less than that or you will blow the breaker on the generator. Wont power 220v as others have already said. Unhook and cap off the incoming power line to protect the lineman.
Yea, it’s pretty simple. One genny with 2 receptacles. 2 short modified suicide cords (male both ends). Feeding 2 house receptacles, 20a, one on each leg of the panel. Main breaker is off, not trying to kill a lineman. The question was specifically the 240, to educate myself. I thought I knew the answer, and you guys confirmed. No AC for me...